The lights are individually switched so would it be okay to exit the two flexes through the flex outlet on the same fcu? The lights have 2 core flex and are Class II
Regards
It would be okay two 0.75mm flexes to a 3A fused connection on the load side, but if the flexes are to buried they will require RCD protection or mechanical protection if buried within wall less than 50mm (and that chase depth will need to be in compliance of part A of building regs).
The flex will also require to within the permitted safe zones and the requirements of BS7671 say that a CPC/earth should be present, so regardless of the Class II fitting I would still run a 3 core. Not only as it will comply to BS7671 but if you ever decided to install a class I fitting you can.