Water hammer from unvented cylinder

This water hammer/pressure spikes is a bit of a mystery to me.

I have a washing machine with a 10M, 15mm (12.5mm ID) pipe run from the mains which has a DCV (double check valve) where I installed a PG today very near the DCV to take a few readings. The filling rate is a measured 8LPM and when the solenoid valve closes after filling, the PG rises from its dynamic pressure of 2.2bar to 2.7bar which is only 0.4bar above its normal static pressure of 2.3bar. Using the attached formula this means that the solenoid valve is taking 1.4 secs to close, I read that a solenoid valve will normally close in 50 millisecs, 0.05secs, if so then the pressure spike should be in the order of 11.3bar? PG ~ 13/13.5bar but I'm not getting anything remotely approaching this, maybe the flexible w/machine flexible hose is taking up the spike?. You can do your own calcs, if interested.

 

Attachments

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top