Wouldn't matter - if you are in the right location you will hear the difference, use that method all the time to locate a problem valve anywhere on a pipe run
Wouldn't matter - if you are in the right location you will hear the difference, use that method all the time to locate a problem valve anywhere on a pipe run
This water hammer/pressure spikes is a bit of a mystery to me.
I have a washing machine with a 10M, 15mm (12.5mm ID) pipe run from the mains which has a DCV (double check valve) where I installed a PG today very near the DCV to take a few readings. The filling rate is a measured 8LPM and when the solenoid valve closes after filling, the PG rises from its dynamic pressure of 2.2bar to 2.7bar which is only 0.4bar above its normal static pressure of 2.3bar. Using the attached formula this means that the solenoid valve is taking 1.4 secs to close, I read that a solenoid valve will normally close in 50 millisecs, 0.05secs, if so then the pressure spike should be in the order of 11.3bar? PG ~ 13/13.5bar but I'm not getting anything remotely approaching this, maybe the flexible w/machine flexible hose is taking up the spike?. You can do your own calcs, if interested.