I HAVE A 7 YR OLD COMBI BOILER ARISTON 27GENUS+.SINCE HAVING
A NEW 4 LITRE EXPANSION VESSEL FITTED 4 WEEKS AGO. I HAVE TO
CONTINUALLY KEEP AN EYE ON THE PRESSURE GAUGE AND FILL UP
WHEN IT DROPS NEAR 0.5 BAR.THERE ARE NO SIGNS OF LEAKS OR AIR
IN RADIATORS AND THE OUTSIDE OVERFLOW IS DRY.HAS ANYONE
ANY IDEAS?
 
Sponsored Links
expansion vessel is too small

should be at least an 8 litre one

fill ch system to 1.5 bar and run ch

what does pressure rise to?
 
THANKS FOR THAT BUT THE FITTER ONLY REPLACED WITH SAME SIZE
WHICH IS A 4 LITRE VESSEL;COULD IT BE FAULTY?
 
according to the boiler MIs


0327 7 L. STANDARDISED EXPANSION VESSEL 65101719

its a 7 litre exp vessel :rolleyes:

your fitter fitted the wrong one :oops:
 
Sponsored Links
THANKS:BUT THE REPLACEMENT VESSEL IS EXACTLY THE SAME SIZE
AS THE ORIGINAL THAT WAS FITTED.ENGINEER USED A FOOT PUMP
TO CHECK THE PRESSURE AND THE OLD ONE WOULD NOT HOLD AIR.
HENCE HE ORDERED A REPLACEMENT FROM ARISTON WHICH IS 4 LITRES
CAPACITY.
 
THE SYSTEM THIS AM HAD SHUT DOWN DUE TO THE PRESSURE
DROPPING TO 0.5;I HARDLY SEEMED TO PUT MUCH WATER IN VIA
FILLING LOOP WHEN GAUGE WAS UP TO 3.2 BAR.STARTED SYSTEM UP
AND WATER IS RUNNING OUT THROUGH OVERFLOW:ALSO LET SOME
WATER OUT VIA RADIATOR THOUGH PRESSURE STILL ABOUT 3.0.LEFT
SYSTEM ON AS FREEZING COLD.COULD GAUGE BE FAULTY?
 
not a faulty gauge, but a faulty expansion vessel its either dead/undersized/needs recharged
see FAQS ANDPLUMBING FIXES AND TIPS FOR EASY TO FOLLOW ADVICE
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top