ok my last post wasn't all that relevant (sorry)!
But I found this to redeem myself:
http://www.eon-uk.com/distribution/...cedures Modules/MODULE 17 Cutouts.pdf[/QUOTE]
Interesting particulally
"Live changing of metal-clad cut-outs, multiphase cut-outs (including Single
Pole Fuse-Units), or cut-outs connected to paper insulated cables is strictly
prohibited."
Which leads to the question of what do they do with the above types of cutouts, cut off the whole street? cut and rejoin the service cable?
edit: seems they do cut and rejoin the service cable
"If in the judgement of the competent person, and/or their supervisor, any of the
above conditions cannot be met, the service must be disconnected from the
main (preferably by cutting the service cable) and the cut-out changed under
'dead' conditions
If in the judgement of the competent person, and/or their supervisor, any of the
above conditions cannot be met, the service must be disconnected from the
main (preferably by cutting the service cable) and the cut-out changed under
'dead' conditions"