Hello everyone, just a quick question about pressure testing pipework.

I have replaced all our radiators and pipework prior to having our boiler changed. Currently they are not connected to any 'live' part of the heating system.
I wish to test the system for leaks before I get a plumber to install a new boiler but I wish to know what pressure I should charge the new pipework and radiators to.

I have just bought an air pressure test gauge with the usual Schrader Valve on it that I will attach to on of the open ends of the pipework.

Is a foot-pump powerful enough to pressurize the system? I don't want to spend hours pumping air in that could be escaping somewhere without me knowing! I have a small compressor with a tyre inflating atachment that I could use - could this be used?


Thankyou,
Mark.
 
Sponsored Links
Joined
23 Feb 2007
Messages
21,178
Reaction score
1,936
Location
Norfolk
Country
United Kingdom
I always use a compressor.

I have a medium size one for testing ch systems. I always test to 3.5Bar for about 1 hour.

I use 3.5Bar so that I have tested the system higher than the 3 Bar prv will blow at.
 
Joined
3 Sep 2005
Messages
3,295
Reaction score
11
Location
Devon
Country
United Kingdom
Definitely can't use a footpump unless you have a lot of time, patience and leg muscles like Popeye :LOL:
 
Joined
8 Jan 2005
Messages
19,003
Reaction score
1,568
Location
Bath
Country
United Kingdom
Air testing should never be carried out unless all the safety measure are put in place prior to doing the test, and in any case you would only need a maximum of 42mb and a standard manometer.

A fitting blowing off at 3.5bar as above would pass right through a human body.
 
Sponsored Links
H

holty

usual recommended pressures 1&1/2 times the working pressure. if any pushfits are used decrease the pressure after 30 mins about a third to test the grab rings.
 
Joined
16 Sep 2003
Messages
7,978
Reaction score
31
Country
United Kingdom
To amplify dia's point, pneumatic testing is DANGEROUS!! Pressure testing on unknown systems should be hydraulic, that way the stored energy is small, but you should take expansion vessels off IMO to ensure there is minimum energy storage.
 
Joined
21 Oct 2004
Messages
19,558
Reaction score
25
Country
United Kingdom
mark_j_k said:
I have just bought an air pressure test gauge with the usual Schrader Valve on it that I will attach to on of the open ends of the pipework.
Take it back, and write out 100 times:

"I must not pressure test a heating system using air."

Is a foot-pump powerful enough to pressurize the system?
As doitall has already pointed out, that would be an unacceptable risky thing to do.
 
Joined
8 Jan 2005
Messages
19,003
Reaction score
1,568
Location
Bath
Country
United Kingdom
usual recommended pressures 1&1/2 times the working pressure. if any pushfits are used decrease the pressure after 30 mins about a third to test the grab rings.

That is an hydraulic test holti and not pneumatic which is roughly equal to 10 x that of water.

3 bar air = 30 bar water, I think and boys will will soon tell me if I'm wrong
 
Joined
3 Sep 2005
Messages
3,295
Reaction score
11
Location
Devon
Country
United Kingdom
Not a dangerous thing to do if the pressure is kept low yet still sufficient for a first stage (and easy) leak check.

A few psi isn't going to cause any problems IMO.

MW
 
Joined
8 Jan 2005
Messages
19,003
Reaction score
1,568
Location
Bath
Country
United Kingdom
Not a dangerous thing to do if the pressure is kept low yet still sufficient for a first stage (and easy) leak check.

A few psi isn't going to cause any problems IMO.

MW

That what I said ;) 42mb and a manometer is plenty and you can blow that with the mouth.
 
Joined
3 May 2007
Messages
5,393
Reaction score
1,147
Location
Surrey
Country
United Kingdom
Air pressure can be maintained by un-soldered but fluxed joints. Water testing will find such problems.
 
Joined
21 Oct 2004
Messages
19,558
Reaction score
25
Country
United Kingdom
Air pressure can be maintained by un-soldered but fluxed joints. Water testing will find such problems.
How does that work? Are you saying that, at the same pressure as a wet test, a dry test will not exert the same force on a loose fitting because of the flux?
_______________

Edit: corrected typo.
 
Joined
10 Apr 2007
Messages
652
Reaction score
14
Country
United Kingdom
flux is water soluble though, so may have a small effect depending on the leak, wouldnt agree with it based on 'unsoldered but fluxed' leaks though.

Sam
 
Joined
12 Feb 2005
Messages
200
Reaction score
0
Country
United Kingdom
That powerflow flux jams the fittings on the pipes so badly I could almost beleive it...and Ive discovered unsoldered endfeed fittings that didn't leak on a vented c/h system before but 3.5 bar would expose ANY lack of solder i'm betting...but I'm not a plumber so what do I know lol
 