    We recently got a new 250 litre 3 coil hot water cylinder installed.
    The tank thermostat is located near the the bottom of the tank and the water never gets warm enough there for the thermostat to switch off the motorised valve that feeds the hot water to the tank.

    Where is the best location on the tank to put the thermostat?

    Thanks.
     
  2. Sponsored Links
  3. 45yearsagasman

    45yearsagasman

    Joined:
    14 Mar 2010
    Messages:
    6,077
    Thanks Received:
    1,083
    Location:
    Norfolk
    Country:
    United Kingdom
    1/3 the way up from the base is ideal. Set it to 60c.
     
    • Thanks Thanks x 1
  4. ALEC1

    ALEC1

    Joined:
    21 Nov 2009
    Messages:
    9,496
    Thanks Received:
    717
    Location:
    London
    Country:
    United Kingdom
    what are the other two coils doing, and indeed what is the top coil doing...?
     
  5. Nephin

    Nephin

    Joined:
    1 Feb 2012
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Top coil is from stove back boiler which is what we use the most.

    The second coil is connected to the oil boiler.

    The third coil is connect to solar panels.
     
  6. mysteryman

    mysteryman

    Joined:
    5 Jun 2010
    Messages:
    1,664
    Thanks Received:
    233
    Location:
    Shropshire
    Country:
    United Kingdom
    Presumably the cyl stat is controlling the heat source to one of the coils? The thermostat should be a little above the coil it controls, and not straight above the flow connection into the coil.

    The old 'one third of the way up' rule was OK for gravity primaries, but it is not a 'one size fits all' rule for pumped primaries or multiple coils.
     
  7. PlumbGas

    PlumbGas

    Joined:
    26 Feb 2011
    Messages:
    398
    Thanks Received:
    57
    Location:
    Surrey
    Country:
    United Kingdom
    Couldn't agree more, if 1 coil then 1/3 up is correct, however your main source of heat is to the top coil and as heat does not travel down then the bottom of the tank will not get hot,
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page