Before i notify building control i want to get my plan sorted and would appreciate some guidance.
I plan to run 1.5mm T&E in surface mount 20mm plastic conduit from under the bath to a cupboard within the bathroom where the CU is.
I will wire directly into the junction box on the whirlpool bath.
refering to the pictures, can i run the cable within the void of the stud wall and enter the 20mm conduit already in place for the underfloor heating?
The CU has a seperate RCBO rated at 16A which i would like to use for the UFH (6 amps) & whirpool bath (4 amps). Is this ok?
If yes, is it correct to install a double pole fused switch between the RCBO & whirpool bath?
The UFH is swithced & controlled by a digital programmer. Should there also be a fused double pole switch for isolation or is it acceptable to wire the programmer direct to the RCBO?
I plan to run 1.5mm T&E in surface mount 20mm plastic conduit from under the bath to a cupboard within the bathroom where the CU is.
I will wire directly into the junction box on the whirlpool bath.
refering to the pictures, can i run the cable within the void of the stud wall and enter the 20mm conduit already in place for the underfloor heating?
The CU has a seperate RCBO rated at 16A which i would like to use for the UFH (6 amps) & whirpool bath (4 amps). Is this ok?
If yes, is it correct to install a double pole fused switch between the RCBO & whirpool bath?
The UFH is swithced & controlled by a digital programmer. Should there also be a fused double pole switch for isolation or is it acceptable to wire the programmer direct to the RCBO?