This is my first post, so please treat me gently (as everyone seems to say).
I'm doing the 1st fix on a self build first floor extension and would like to incorporate wiring for a Whirlpool bath. I have read most of the posts on this subject, but would appreciate knowing if what I propose to do is likely to be acceptable.
I am planning to spur off a new ring main that I am installing in the adjoining bedroom, fit an RCD FCU on the spur and route the cable through the stud wall to either an IP68 rated waterproof junction box on the wall under the bath, or to a IP67 waterproof cable joint, to which the supply cable from the motor can be connected.
Now the questions:
1.) The ring main will be connected to a split load CU on the 30mA RCD protected side, so is an additional RCD protected FCU necessary, or would a normal FCU be OK?
2.) Is a triple pole isolator required as well as the FCU?
3.) Will it be acceptable to position it on the wall above the door IN the bathroom? From what I've read it would seem that as long as its above 2.25m and more than 0.6m from the bath or basin that it is "out of zone".
Thanks for any help that I may receive.
(P.S. Building Control are already notified)
I'm doing the 1st fix on a self build first floor extension and would like to incorporate wiring for a Whirlpool bath. I have read most of the posts on this subject, but would appreciate knowing if what I propose to do is likely to be acceptable.
I am planning to spur off a new ring main that I am installing in the adjoining bedroom, fit an RCD FCU on the spur and route the cable through the stud wall to either an IP68 rated waterproof junction box on the wall under the bath, or to a IP67 waterproof cable joint, to which the supply cable from the motor can be connected.
Now the questions:
1.) The ring main will be connected to a split load CU on the 30mA RCD protected side, so is an additional RCD protected FCU necessary, or would a normal FCU be OK?
2.) Is a triple pole isolator required as well as the FCU?
3.) Will it be acceptable to position it on the wall above the door IN the bathroom? From what I've read it would seem that as long as its above 2.25m and more than 0.6m from the bath or basin that it is "out of zone".
Thanks for any help that I may receive.
(P.S. Building Control are already notified)