Why does this switch provide a 56 AC voltage

Discussion in 'Electrics UK' started by Jupiter01, 22 Sep 2020.

  1. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,915
    Thanks Received:
    39
    Country:
    United Kingdom
    I was using my 2 pole tester on a light switch and intrigued by why the following is happening.
    Here's the light switch in question:

    upload_2020-9-22_10-14-42.png

    It's the left switch I was investigating.

    The closest cables relate to the switch in question:
    upload_2020-9-22_10-15-57.png

    The light illuminates with the operation of this switch. When the light is off, I get 50 AC on these wires and when I switch it on, I get no reading.

    Is this expected?
     
  2. Sponsored Links
  3. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    4,110
    Thanks Received:
    828
    Location:
    Durham
    Country:
    United Kingdom
    50 volts AC relative to what? Is your tester one of those things with a series of LEDs up the side of it?
     
    • Like Like x 1
  4. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,915
    Thanks Received:
    39
    Country:
    United Kingdom
    Yes, it's a Fluke 2 pole tester with the LED lights
     
  5. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,915
    Thanks Received:
    39
    Country:
    United Kingdom
    one of these:
    upload_2020-9-22_10-33-20.png
     
  6. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,131
    Thanks Received:
    2,482
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Assuming you are measuring voltage difference between the two terminals on the switch

    One probe on Live and the other on Switched Live

    The Switched Live is connected via the lamp to Neutral

    With the switch OFF the lamp will pull the Switched Live towards the Neutral potential. A filament lamp is low impedance and will pull Switched Live hard to Neutral potential. An electronic lamp is higher impedance and will not pull Switched Live to Neutral as hard as a filament lamp.

    The voltage on the Switched Live will depend on the impedance of the lamp and the impedance of the test instrument.
     
    • Like Like x 1
  7. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    4,110
    Thanks Received:
    828
    Location:
    Durham
    Country:
    United Kingdom
    • Thanks Thanks x 1
  8. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    47,631
    Thanks Received:
    3,099
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    If you mean you are measuring the voltage across the switch then, yes, you would expect to measure a potential difference across it when the switch was 'off', but no voltage when it was 'on' (shorting out your test instrument).

    Were it a high impedance tester, you would expect to see ~230V across the switch when it was 'off'. If the tester is deliberately 'low impedance', you would see less voltage, since the 230V would then be 'shared' between your tester and the load (light).

    Kind Regards, John
     
  9. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom