Q: would a single 6mm radial wire be safe, I don't feel confident with fitting 2.5mm again, to close for comfort. Any advise guys.
Breezer yes a loose connection could be the problem here but all screws are tight on the mains. Could a loose connection on the appliance be the cause. Or could heavy use of the system be the real reason as all three have been running together fairly regular.
Q: Could the fact that they are all at one end of the circuit be putting more strain on one of the wires, therefore all the load running through that wire.
Q: Would it be wiser to use the spare space and create a separate ring for one of the appliances, and place the other two together there for reducing the load. or would just one bigger cable do it.
plugwash said:
a few more questions
1: is the burning only in a small area near accessory or joint
2: are the loads all close to the same end of the ring?
personally if you are going to rewire the appliances and you have the space in your CU i would go for 3 seperate 16A 2.5mm radials its only a tiny bit more cable than a single ring after all
in answer to your question
1.- the burning is on live wire only at mcb end [only one of the wires]
2.- yes, all three sockets are next to each other 1 double, 1 single, could say that they are at middle of ring.
3.- possible but only got space for one more mcb.
plugwash said:
only if the loading is in the exact centre of the ring
the IEE say each cable in a ring should be rated for at least two thirds of the fuse/breaker rating
this is ok in most cases but there could still be problems if a lot of high power appliances are located close to one end
A: 32A MCB, 27A cable rating should have been more than enough, unless the 30A load is not split evenly. Is that what you mean
ban-all-sheds said:
As has been pointed out, it's a ring circuit.
Read this:
http://www.iee.org/Publish/WireRegs/Amd1andRC.pdf[/QUOTE]
Thanks the article was very useful, recommend for others to read.