Multiplex said:
Is it okay to wire a ring like this?
In my garage I'm putting in a radial circuit. Is it okay to run a cable round the beams and drop a single cable down the wall for each socket similar to the picture above? Does that affect the cable rating at all (using 2.5mm)?
Thanks,
Simon.
Wiring the circuit as you suggest defeats, to a great extent, the point of having a ring.
The idea of a ring is that a low-rated cable can, using a ring, supply a much higher current, with half the current being drawn equally from both sides of the ring. So that the maximum (theoretical) rating of a 2.5sqmm ring would be about 50amps - more than enough to cope with someone operating every conceivable home electrical appliance at once.
However, since every outlet in your circuit will be on a spur, ultimately the ring serves no purpose, since the current is divided around both halfs of the ring, only to be recombined as it enters the spur cable. Therefore, assuming you are using 2.5sqmm, the maximum rating of the circuit, despite having a ring incorporated into it, is still only 25amps. And you would then have to use a breaker that is 25amp or less.
I suggest you either go the full whack and install a proper ring, with no spurs, or else simply daisy-chain the sockets on a single cable.
Also, what you need to consider is what will you be using these eight double sockets for? If you will have a number of high-load appliances on the circuit at once, you should consider opting for a proper ring.