Hi all,

Can anyone help me with the wiring on a ideal logic the boiler only has L,N, timer and stat just need to know where they go to on the siemens??
 
Sponsored Links
Hi all,

Can anyone help me with the wiring on a ideal logic the boiler only has L,N, timer and stat just need to know where they go to on the siemens??

The boiler terminals are labelled: Frost Stat (2), Mains (3) and Room Stat/Timer (2).

Use a 4 core (plus earth - not used) heat resistant cable, e.g Tower brand 0.5mm or 0.75mm from B&Q. Make the earth wire safe by cutting back to the outer cover at both ends.

Wiring is:

Boiler L to RF L (brown)
Boiler N to RF N (blue)
Boiler Stat/timer to RF Lx (any colour)
Boiler Stat/timer to RF L1 (any colour)

Remove link between the two stat/timer terminals.
It does not matter which way round the stat/timer terminals connect to the RF Unit.
 