You have not said yet if you have a multimeter. I will assume that you have.
It is best to do as much inspection and test with the circuit dead as possible, before you start live testing, which is more likely to lead to injury or death.
Cut the power to all the sockets on the circuit that you have a problem on.
Test that they are now dead.
You say that you have a junction box. Take the lid off and see how many cables go into it; and check that all the cores are firmly connected and undamaged. Also see if all the reds go to one terminal; all the blacks to another; and all the G&Y (or bare
) connected to another. Report back here if not.
If the junction box seems to be correct:
Take off each of the socket faceplates (don't disconnect any wires yet) and identify if each has two cables; three cables; or one cable connected to it.
Make a sketch of your floor layout and draw the socket positions, marking the state of each. The normal number of cables to a socket on a ring is two.
Observe if the cores within each cable are firmly connected and undamaged.
Come back and tell us how many of your sockets have two cables to them, and how many have a different number.
Also if you have detected any damaged or badly connected cores.
We can talk you through continuity testing next.