Im replacing the controller and sorting out the very very messy wiring linking the system together but im unsure where the froststat should go
I have the S plan system and all electronic parts are Honeywell, valves, controller and both cylinder stat and frost stat
Am i right in saying that it goes to permanent live and the neutral side going to the CH ON terminal block at my junction box. Im assuming this would override any signal from the controller to tell the system to turn on/off and would turn the heating on if it went below 5 degrees or whatever
Cheers chaps, Dave