wiring problem glow-worm 18 sxi help!!!!!!! help again!!!!!

Joined
25 Mar 2011
Messages
11
Reaction score
0
Location
Blackpool
Country
United Kingdom
well it worked for a few days now i'am getting a f1 code.reset and boiler fires for about 5 seconds then go's out,i can see the flame in the sight glass it fires again same thing,it tries to fire again and locks out and i get the f1 code? it has been working great? fan is working,boiler is lighting(for 5 seconds) don't know about the pump.thanks again guys.shane.
 
Sponsored Links
Whilst you know the history, I do not!

That seems to be a lack of flame detection and that needs a registered gas engineer.

All you could do is check that no wires have been disturbed from the combustion chamber ( do not open ) to the PCB.

On condensing boilers a blocked and so full condensate trap can cause this problem.

Tony
 
cheers tony,the condensate trap was full of crap so i cleaned it all out and the boiler stayed lit on the 2nd try fingers crossed i know the glow-worm boilers are not the best.whats the float for? i had a look at it and could't work out what it does.no micro switchs or wiring on the trap but it was overflowing.thanks again shane.
 