Hi all,
Hope you can help before I start ordering expensive parts.
Just recently the hot water temperature fluctuates every 30-60s or so.
This happens at every tap/shower.
I checked the boiler and as hot water demand comes, the boiler is firing up., Then eventually the boiler switches off then re-starts etc in this cycle.
I checked the flow turbine and it seems ok.
I checked the domestic hot water sensor. Before water flow, this sits around 4.0vDC. As the hot water is supplied it drops steadily to 3.2vDC, and this is when the boiler switches off (ie flame goes out).then as the temp cools, the voltage rises to 3.8vDC, then the flame re-ignites. It then continues on this cycle.
Does anyone know if these voltages are normal for this sensor ?
I replaced the control PCB about 2 years ago, so this is newer than the rest of the boiler.
Thanks for your help.
Tbone.
Hope you can help before I start ordering expensive parts.
Just recently the hot water temperature fluctuates every 30-60s or so.
This happens at every tap/shower.
I checked the boiler and as hot water demand comes, the boiler is firing up., Then eventually the boiler switches off then re-starts etc in this cycle.
I checked the flow turbine and it seems ok.
I checked the domestic hot water sensor. Before water flow, this sits around 4.0vDC. As the hot water is supplied it drops steadily to 3.2vDC, and this is when the boiler switches off (ie flame goes out).then as the temp cools, the voltage rises to 3.8vDC, then the flame re-ignites. It then continues on this cycle.
Does anyone know if these voltages are normal for this sensor ?
I replaced the control PCB about 2 years ago, so this is newer than the rest of the boiler.
Thanks for your help.
Tbone.