• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Worcester boiler shutdown after a few hours

Get a thermometer on the flow away from the heat exchanger to see what the water temp is getting up to.

If its getting up past the 80oC then could be the boiler stat/ thermistor letting it run to long hence tripping the overheat at 100oC

Also could be a slugish pump not getting the water away from the boiler fast enough or some sludge in the boiler.
 
Hi Superdupergasman

That's why I am confused - the overheat ISN'T tripping at all - and the boiler can be relit without touching the overheat ....

Thanks for your input tho.
 
Mmmmm

I sent you one too ... but there is nothing now showing in my outbox .... v v odd! :) Did you get it?
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top