Worcester boiler shutdown after a few hours

Get a thermometer on the flow away from the heat exchanger to see what the water temp is getting up to.

If its getting up past the 80oC then could be the boiler stat/ thermistor letting it run to long hence tripping the overheat at 100oC

Also could be a slugish pump not getting the water away from the boiler fast enough or some sludge in the boiler.
 
Sponsored Links
Hi Superdupergasman

That's why I am confused - the overheat ISN'T tripping at all - and the boiler can be relit without touching the overheat ....

Thanks for your input tho.
 
Sponsored Links
Mmmmm

I sent you one too ... but there is nothing now showing in my outbox .... v v odd! :) Did you get it?
 