Worcester Bosch 30CDi Regular & DT20 Programmer

Discussion in 'Plumbing and Central Heating' started by Mikesm11, 12 Oct 2011.

  1. Mikesm11

    Mikesm11

    Joined:
    12 Oct 2011
    Messages:
    2
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    Hi,

    I want to add a DT20 programmer to a greenstar 30CDI regular boiler previously contolled by an external Horstman programmer through a 10 contact wiring centre. I can not find on WB literature site any instruction of how the wired 3 port valve, room stat and Tank stat should be wired so as to work with the built in DT20. Can anyone help?

    Many thanks in anticipation
     
  2. simond

    simond

    Joined:
    26 Oct 2004
    Messages:
    5,232
    Thanks Received:
    465
    Location:
    Surrey
    Country:
    United Kingdom
    You can't fit any plug in Worcester controls to a 30CDi conventional. It is external controls only, wired through Ls and Lr.

    To be frank, Worcester's controls aren't up to much anyway, being based on Drayton Invensys stuff; you'd be better off using Honeywell parts.

    3 port valve is undersized from a hydraulic point of view for a 30Kw boiler, by the way.
     
  3. Sponsored Links
  4. Mikesm11

    Mikesm11

    Joined:
    12 Oct 2011
    Messages:
    2
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    Many thanks simond.

    I contacted the company who supplied the DT20 today and they said the same and apoligised that the salesman gave me bum info, they have refunded me so will get a Honeywell to replace the faultly Horstman.

    Are you able to say what should have been fitted instead of a 3port valve? Should it have been two 2-port valves, one on the water and one on the CH?
    S plan layout?

    best wishes

    MikeSM11
     
  5. simond

    simond

    Joined:
    26 Oct 2004
    Messages:
    5,232
    Thanks Received:
    465
    Location:
    Surrey
    Country:
    United Kingdom
    Yes, Mike, the 2 port valves give less resistance to flow.

    You must also fit a bypass (such as the Honeywell DU144 or DU145) to allow the boiler pump overrun to work when both valves are closed.
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page