Worcester greenstar 18ri install

Discussion in 'Plumbing and Central Heating' started by foxhole, 10 Oct 2011.

  1. foxhole

    foxhole

    Joined:
    14 Mar 2006
    Messages:
    14,191
    Thanks Received:
    1,531
    Location:
    Kent
    Country:
    United Kingdom
    Just had the above installed but having problem with control, MI contradict wiring instruction for boiler with that of honeywell guide, original wiring does not work and following MI to wire pump thru boiler the boiler is live and running with controller live but turned off?
    Plumber has tried replacing both three port valve actuator and controller [danfoss fp 715si].Have also replaced wiring from controller to boiler to ensure no cable damage.
    Any ideas?
     
  2. simond

    simond

    Joined:
    26 Oct 2004
    Messages:
    5,233
    Thanks Received:
    465
    Location:
    Surrey
    Country:
    United Kingdom
    It is difficult to understand your description of the problem.

    We fit an Ri pretty much every week of the year, and the wiring is very straightforward.

    You appear to be backfeeding the boiler via the pump overrun cable, but the description is so vague it is hard to tell.

    What amazes me is that you mention an 'installer'. I'm one of those and my customers would not dream of letting me leave a system wired incorrectly...... how come this person can walk away from a problem of his making?

    If I was Agile i would be speculating the nationality of the installer and his professional status with Gas Safe Register.

    Hope it was a cheap job, I take it there was no powerflush machine in evidence either? Actually, no point asking really.
     
  3. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,046
    Thanks Received:
    9,421
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Another quality install :LOL:

    Can you re-post the question, but so that it makes sense? tah.
     
  4. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,560
    Thanks Received:
    4,510
    Location:
    London
    Country:
    United Kingdom
    Why not start by telling us something about the installer?

    Would he be able to read the Sun or the Mail and enjoy one or other of those papers? ( or even the Telegraph? ).

    If anyone reminds me in the CC I will tell a story about papers.

    How do you know that he is Gas Safe registered?

    As Simon has said, how is it that he can install the boiler and then leave you with it not working correctly?

    Now the payment? Surely you are not going to pay him when he has not completed the job correctly?

    If he cannot do it properly then all he has to do is call an industry colleague ( and pay him ) to sort it out! There are thousands who will be happy to do that!

    Tony
     
  5. foxhole

    foxhole

    Joined:
    14 Mar 2006
    Messages:
    14,191
    Thanks Received:
    1,531
    Location:
    Kent
    Country:
    United Kingdom
    I made no mention of him leaving without getting it working, he was here from 8am to 8pm , he installs these daily and never came across this problem before, should have been a straight swop for the old boiler, but after much head scratching found that a link was required which is not mentioned in honeywell quide or the MI.
    It's now working fine, has cleaner in system and he will be returning to flush system in a couple of days.
    He is gas safe registered and has installed boiler at my other property without hitch.
    I was simply asking for guidance not criticism.
     
  6. Jake1886

    Jake1886

    Joined:
    28 Jul 2010
    Messages:
    470
    Thanks Received:
    44
    Location:
    London
    Country:
    United Kingdom
    Welcome to diynot.com :D
     
  7. lawrance

    lawrance

    Joined:
    27 Jul 2008
    Messages:
    739
    Thanks Received:
    113
    Location:
    Surrey
    Country:
    United Kingdom
    So basically you have got crap running round your system and the hex on an ri is a big magnet for it, hope your system aint too dirty cos that cleanser aint gonna do sod all for that hex.
    If the guy cant wire a simple boiler then he defo cant flush a system properly......good luck with your boiler cos you are gonna need it.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page