Worcester Greenstar 30Si - intermittent hot water

Joined
4 May 2008
Messages
95
Reaction score
4
Location
Lincolnshire
Country
United Kingdom
Hi All,
Looking for some advice regarding my Worcester Greenstar 30Si. When there is a demand for DHW the water is hot for a few seconds, then cold, then hot etc...
The thing is that I had the same thing around this time last year and called out a central heating engineer. The engineer diagnosed the problem as a scaled up heat exchanger and was all set to remove and clean/replace the exchanger until he discovered that due to the boiler design it would be extremely time consuming to remove.
Instead he suggested adding a limescale remover to the CH system (directly into a radiator) and then running the central heating for a couple of days.
Now, I don't know anything about central heating, but I could never understand the logic in this method - how descaling the CH would fix the issues with the DHW.
However, this approach worked perfectly - after the CH had been on for 12 hours the DHW problem had gone and everything has been fine for 12 months until the last couple of days.
My question is, is there a good reason why this should have worked? if so, was it due to adding the limescale remover, or was it just due to running the CH?
 
Sponsored Links
The limescale remover (whatever that was) will do nothing if added to the CH - the water in there is continually recirculated, so you won't get any scale buildup.
Therefore, if nothing else was done, it was running the CH for 12 hours which fixed the problem. Possibly there was some other blockage or restriction which was cleared by using the CH.

Any scale would be on the other side of the heat exchanger, where the cold mains water enters and is then heated before going to the outlets.

Heat exchangers are easy to descale once removed.
If removing it is considered too difficult or time consuming, they can be descaled without removing if you have the correct machine.
 
The limescale remover (whatever that was) will do nothing if added to the CH - the water in there is continually recirculated, so you won't get any scale buildup.
Therefore, if nothing else was done, it was running the CH for 12 hours which fixed the problem. Possibly there was some other blockage or restriction which was cleared by using the CH.

Any scale would be on the other side of the heat exchanger, where the cold mains water enters and is then heated before going to the outlets.

Heat exchangers are easy to descale once removed.
If removing it is considered too difficult or time consuming, they can be descaled without removing if you have the correct machine.

Thanks for the reply, - I must admit that I couldn't figure out how adding the scale remover (actually X200 noise reducer) to the CH could have improved the DHW, but as it appeared to work I thought I must be missing something!

I will try running the CH for a bit to see if there is any improvement, and if not look at getting an expert in to take a look.
 