Worcester Heatslave 11 oil boiler adding inhibitor to system

Joined
16 Oct 2010
Messages
31
Reaction score
0
Location
Yorkshire
Country
United Kingdom
I had this oil boiler fitted last year and on returning from a holiday switching on the central heating for the first time over the summer last week I noticed one of the radiators needed bleeding. I bled it but being very tired I didn't tighten the bleed valve sufficiently and some water leaked out. I immediately turned the heating off. The pressure is now showing just above 0 cold. I want to add inhibitor to the system before topping up the pressure with the loop.

With my old Camray 5, I just used to release the pressure with the pressure relief valve and drain some water out of one of the radiators and then add the inhibitor into the top of the radiator before topping up the pressure. Can I just do the same with this boiler or what do you suggest ?
 
Sponsored Links
Best to leave the PRV alone, I like to inject Fernox F1 through a rad bleed valve and at the same time leave another bleed open to equalise the pressure.
Once done, up the pressure through the filling loop up to 1 bar.
John :)
 