Worcester Heatslave 26/32 (Oil fired) - water far too hot

Joined
11 Jan 2009
Messages
5
Reaction score
0
Country
United Kingdom
You may rmember my earlier tale of woe but this boiler crapped out electrically over Christmas and has had a new PCB, new flow switch, new expansion tank, new oil solenoid. This all cured the original problem. During adjustment, the engineer could not get the CO levels right and changed burner nozzle. Slight improvement but still went to hell when burner box cover replaced. Eventually found insulation plates from balanced flue had dropped into inlet. Cleaned out and CO OK and boiler operated. Worcester said boiler OK without insulation plates; or is it?
Since then - and intermittently but more often than not - water is so hot as to be dangerous. Thermostats on front of boiler have no effect (you can feel the heat radiating off the boiler from a metre away). If I pull the sensor out of the heatslave tank, the thermostat clicks OK. Put it back in and it seems as if it has no set point - it has no effect (it cannot get any hotter!!). Sod's Law- the boiler behaved when engineer came to look at it.
Any ideas?
 
The thermostat is faulty. Replace it. It is a safety control, not to be treated lightly.
 
Hi Oilman,
done that - still the same. Should also mention the central heating stat also suffers in the same way.
 
changed the limit stat today - the only thing left is the PCB replaced earlier this year. The problem only manifested itself after that.
Thanks for all replies.
 
limit stat kicks in if boiler stat fails or to protect boiler from dry fire.
so if it was the limit stat at fault it would be because other stat also failed also which seems unlikely
 