hi i have a y plan valve that works fine on ch hw but when on ch only its putting 240volts onto the hw opening up the valve for both , the pump and y plan was changed recently, the ch was comin on with hw replaced timer and that stopped that, the boiler doesnt fire up on hw when ch roomstat is turned down but still puts 240 onto the valve???any ideas
yes its wired wrong or the replacement programmer is
the valve will
always have 240v on it unless power is off at the spur
ch off hw off....240 on grey
ch on hw off ...240 on grey(permenant)and white and orange(depending on demand)
ch off hw on.....240 on grey
or orange depending on demand
ch on hw on....240 or 115ish on gray depending on demand/position of valve and 240 on white and orange depending on demand
to add to this there will also sometimes when white grey or orange will be at 0v (depending on demand) but as I said earlier there will never be a time when there is not 240 on at least one colour (unless the system is turned off at the spur),
Matt