Yes, due to parallel paths.You test Ze (or should) with the main earthing conductor disconnected from the CU, but Zs is tested with the Main Equipotential Bonds in place.
 
yes thats right. main earth disconnected. test between phase incoming,consumer unit off and earth. test Zs with plug in loop tester
 
I have read that it is better to determine a realistic and therefore more useful Zs value with the main earth bonding disconnected. Does anyone do it this way?
 
Podooser said:
I have read that it is better to determine a realistic and therefore more useful Zs value with the main earth bonding disconnected. Does anyone do it this way?

Although that would make sense, it is not the correct way to do it as you must have bonding in place as the Earth fault loop impedance test can introduce voltages on to exposed metalwork.
Anyone in contact with this metalwork could receive a shock.
 
Ze test should be done with the earthing conductor disconnected. Zs should be done with the main bonding and equal-potential bonding conductor disconnected. so as to remove parallel paths.

Ze TT SYSTEAMS 21 ohms
TN-C-S 0,35ohms
TN-S 0,8 ohms
 
Ze test should be done with the earthing conductor disconnected. Zs should be done with the main bonding and equal-potential bonding conductor disconnected. so as to remove parallel paths.

Ze TT SYSTEAMS 21 ohms
TN-C-S 0,35ohms
TN-S 0,8 ohms

1]Why resurrect an old post ?

2]Why post incorrect advice ?
 
And 21ohms for a TT is the DNO's declared maximum for their side of the TT, yours is likely to be far higher. Anything below 200ohms is considered stable.
 