hi is it possible to have a Ze reading thats higher than a Zs reading? 40ohms Zs and 90 Ze.
Podooser said:I have read that it is better to determine a realistic and therefore more useful Zs value with the main earth bonding disconnected. Does anyone do it this way?
Ze test should be done with the earthing conductor disconnected. Zs should be done with the main bonding and equal-potential bonding conductor disconnected. so as to remove parallel paths.
Ze TT SYSTEAMS 21 ohms
TN-C-S 0,35ohms
TN-S 0,8 ohms
Zs should be done with the main bonding and equal-potential bonding conductor disconnected. so as to remove parallel paths.