Zs value and loose connection

Joined
17 Jun 2009
Messages
75
Reaction score
0
Country
United Kingdom
If you have a zs value that is within the allowed regulation is it still possible to have a loose connection?

Sorry about some starting so many threads. I just worry loads. :(
 
Its a 10mm2 cable for a shower and i took one reading and it said 1.79 then another and it gave me 0.64.
 
Does your tester have a valid calibration certificate and a recent set of batteries?
 
How long? 1.79 ohms as an R1+R2 value is a fairly long length of 10mm, as is 0.64 ohms.
 
Only about 20 m long and yeah it was calibrated about 2 months ago, would old batteries be giving readings like that?
 
Have you test the external impedance of the installation?

Maybe try your tester on a socket a few times and see if your readings are consistent.
 
I don't think you should have started this second thread. Continuing the old one where these questions were answered already would have been so much better.
 
my fluke gave random readings which turned out to be old batteries, the battey low light wasnt even on!
 
Yep, old batteries can give funny readings even if the battery indicator is showing them as being ok.
 
Seemed to have sorted it now when i got back to the job i decided to run another zs test on the shower only this time it gave me 3.??, so then i went round and checked every connection which were also tight. Then after a bit of head scratching i decided to change the rcbo for an mcb and got i reading of 0.36 (i also had a r1-r2 reading of 0.12 and ze of 0.24) i did this test again and also got 0.36. I then put the original rcbo in again and failed to get a reading at all before it tripped out, so in the end i left it on a 32a 30mA rcbo for the weekend which was giving me a bit higher readings but i was doing it on the trip test on my tester so therefore was expecting it.
 
R1+R2 of 0.12 ohms isn't bad.
I take it you were using D-Lock or a low current type measuring device? These generally do give a higher than normal reading, especially if there is any noise on the system.
 