I'm pulling my hair out on some issues with my newly installed Vaillant system. The installer has been responsive but I think the issues are beyond them so seek the input of specialists on this forum.
Details:
• Ecotech 428
• Open Vent condensing boiler
• Fully pumped system (2 motorised valves)
• DAB VA55-130: 3 speed pump on setting 2
• Power flushed prior to installation
• D0 setting = 30
Issue 1
It generally works fine (except see 4) when both the hot water and heaters are selected. However on Hot Water only it starts up for about 30 secs and then turns off for over a minute. Hence it takes about 45 mins to get the hot water up to a reasonable temperature.
Details: D41 quickly fires up from 55 deg C to ~ 76 deg C taking ~ 30 secs, the flame cuts out and only fires up again when it cools down to 55 deg C. The temp difference between D41 and D40 is about 13 deg C. I've tried different pump speeds to no avail.
Is this intermittent firing normal? I can't see it being a good thing?
Issue 2
After the system shuts down (on either hot water or heating) the pump overrun kicks in with hot water going into the expansion tank in the loft for about 4 mins. It gets quite frothy and I'm guessing aerating the water can't be good for corrosion?
There is an automatic bypass fitted about 3 metres away from the boiler. Even opening this to minimum DP does not prevent the overrun into the expansion tank on shutdown so I can't really understand what it does? I wonder if issue 3 is preventing the pressure build up and so stopping the valve doing its job properly?
Issue 3
I note that the location of the open vent/ cold water feed straddles the hot water cylinder. Would have thought it should be on the pump suction per instruction manual. What's the consequences of having this set up?
Issue 4
I’ve just started getting the dreaded S53 error message in the mornings when on auto timer which prevents it running up. For some strange reason it then works fine about 30 mins later when I activate remotely.
Comments appreciated
Details:
• Ecotech 428
• Open Vent condensing boiler
• Fully pumped system (2 motorised valves)
• DAB VA55-130: 3 speed pump on setting 2
• Power flushed prior to installation
• D0 setting = 30
Issue 1
It generally works fine (except see 4) when both the hot water and heaters are selected. However on Hot Water only it starts up for about 30 secs and then turns off for over a minute. Hence it takes about 45 mins to get the hot water up to a reasonable temperature.
Details: D41 quickly fires up from 55 deg C to ~ 76 deg C taking ~ 30 secs, the flame cuts out and only fires up again when it cools down to 55 deg C. The temp difference between D41 and D40 is about 13 deg C. I've tried different pump speeds to no avail.
Is this intermittent firing normal? I can't see it being a good thing?
Issue 2
After the system shuts down (on either hot water or heating) the pump overrun kicks in with hot water going into the expansion tank in the loft for about 4 mins. It gets quite frothy and I'm guessing aerating the water can't be good for corrosion?
There is an automatic bypass fitted about 3 metres away from the boiler. Even opening this to minimum DP does not prevent the overrun into the expansion tank on shutdown so I can't really understand what it does? I wonder if issue 3 is preventing the pressure build up and so stopping the valve doing its job properly?
Issue 3
I note that the location of the open vent/ cold water feed straddles the hot water cylinder. Would have thought it should be on the pump suction per instruction manual. What's the consequences of having this set up?
Issue 4
I’ve just started getting the dreaded S53 error message in the mornings when on auto timer which prevents it running up. For some strange reason it then works fine about 30 mins later when I activate remotely.
Comments appreciated