Hello,
Fantastic forum guys! we recently moved house and are doing some changes to the kitchen, we are replacing a built-in oven and a steel plate hob for a slot-in hotpoint HUE61 cooker which according to the book has a max load of 10.7Kw the existing wire running to the cooker is 6mm2 and the circuit is protected by a 32amp MCB in the consumer unit.
Would this need to be changed to 10mm2 cable and a 45amp MCB? the length of cable from the CU to the cooker is approx 10 meters and runs under loft insulation.
The conduit running from the loft to the CU and from the loft to the cooker is only 20mm so wouldn't allow 10mm2 cable to run down it I would have to re track the walls etc to fit new conduit so if possible I'd like to stick to the 6mm2 cable.
I dont have any manuals for the existing built in oven or hob to compare against.
Advice please?
Fantastic forum guys! we recently moved house and are doing some changes to the kitchen, we are replacing a built-in oven and a steel plate hob for a slot-in hotpoint HUE61 cooker which according to the book has a max load of 10.7Kw the existing wire running to the cooker is 6mm2 and the circuit is protected by a 32amp MCB in the consumer unit.