He says you have to make sure the dno cables and head comply with the regs - the regs do not apply to those parts.
This bit? If so then he has a point.
131.8 No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate.
The Regulation requires that if you plan to make any changes, the existing installation must be in such a condition which will be suitable for the intended alteration. As is stated, this includes:
■ the equipment belonging to the distributor - e.g. the condition and size of the supply cable, the District Network Operator's (DNO) cutout (sometimes referred to as the "head"), metering equipment, supply and meter-tails
■ distribution equipment -switchboard, consumer unit, etc., and
■ the earthing and bonding arrangements.
If any part of the installation intended to be altered is not suitable it must be brought up to standard - the standard being BS 7671:2008.
Where equipment belonging to the distributor or metering company is not suitable for the altered circumstance, i.e. the tails are undersized or the equipment is damaged with exposed live parts, the installer must ensure that the equipment is in a safe condition before undertaking the installation work. In most cases, it will be necessary to arrange for the distributor and/or metering company to attend site and make the changes; this type of work will usually incur a charge.