question about ring calculation...
19 Sep 2007
Staffordshire
just a quick question while i was doing some calculation a ring main on a tns system
Wired in 2.5mm twin and earth ( r1+r2 value 19.51 m.ohm/M )
Approx length of run 35 Metres
Type B circuit breaker max E.F.L. 1.16ohm (on site guide)
Zs = 0.8 + (0.68 ) = 1.48ohm (exceeding max value for breaker)
is it the fact that circuit will have r.c.d. protection or because its a 'ring' mean this circuit is ok even though the e.f.l is high? or is it not ok and ive missed something?
35M 2.5 twin and earth wired as a ring final:
r1 = (35x7.41)/1000 = 0.26ohms
r2 = (35x12.10)/1000 = 0.42ohms
R1+R2 = (r1+r2)/4
R1+R2 = 0.17ohms
Zs = Ze + (R1+R2)
Taking Ze to be maximum of 0.8ohms for a TN-S
Zs = 0.97ohms (maximum calculated at design stage without knowing true Ze)
Because the fault will not cover the entire ring length as it stands as a measured value end end. the true earth fault path is the R1+R2 value.