Very strange fault
3 Jul 2007
Manchester
Small flat, TN-C-S supply, Ze 0.19ohms.
16th edition installation, split RCD board.
Non RCD
1 - Boiler (16A)
2 - Lights (6A)
3 - Security Alarm (6A)
RCD
1 - Oven (32A)
2 - Sockets (32A)
3 - Sockets (32A)
IR for all circuit (L&N - E) >299Mohms (no problem there).
30mA RCD trips within maximum time, trips at 21mA on ramp (no problem there).
Zs for lighting circuit 0.98ohms (no problem there).
Customer calls to say when he switches his outside light off which is fed from the lighting circuit (W2, not protected by RCD) the RCD trips.
He demonstrates this and yes, the RCD does trip with all MCB's still energised.
Split board wired correctly, no neutrals crossed over. The RCD only trips when the outside light is switched off.
I measured IR between circuits for separation and again, all read >299Mohms.
Any idea's?
Have you checked the tightness of the incomming connections, especially the neutral around the cutout / meter / main switch?
Also tightness of connections onto the busbar etc?
Yes, everything tight, all busbar tags correctly gripped by MCB terminal.
How is the switch wired?
What make of RCD - does it have a functional earth?
Has the RCD tripped since the lights were installed, or has it started of it's own accord?
The only think I can think of is something like a spike of back EMF as the magnetic feild in the chokes of the 2D lights collapses.
Having said that, it's getting a bit outside my knowledge base, so maybe someone else could say yay or nay?
Started to trip recently. Also tripped when I had both 2D fittings disconnected :?
So it tripped as you switched the switch off, even with the lights disconnected?
Was there any load at all on the switch at that point?
It does sound very odd indeed :?
Yes though I had to operate the switch numerous times to trip the RCD with the lights disconnected.
At that point there was no load at all on the switch.
I'm just struggling to think how a circuit on the non RCD side of the board could trip the RCD.