Rads getting hot when they shouldn't
yes take the lid off and have a look.
when you put the hw on the valve will fall to hw only by a spring not the motor.
hw only is its relaxed position where it would say if you removed all power from the valve.
the motor will only come in to play if you want hw/heating or heating only.
jeez yer such a star
When I switch to heating only nothing happens the motor only moves if i switch to hw only
that don't make sense.
if you isolate the fused spur the valve should fall to relaxed position.
hw only port open.
turn hw off at programmer and heating on and calling at wall stat.
fused spur on and the motor will wind over to heating only port.
hw only port open.
Nope the motor only moves with the hw switched on - it's almost like it's reversed - never had this problem before
can't say much i can't see it. but that ain't right as a motor can't open to hw. the spring does it.
Me again - just been to B&Q they do a replacement Sunvic three port valve for £40 - is this something a novice could do or do I need a plumber - I assume I need to drain the system down ?
You may not need to change the complete valve - just the actuator (box on top).
1. Have you checked that the valve is the correct way round? The port marked A should go to the radiators; the port marked B to the HW cylinder. If it's the wrong way round, that needs to be put right first. You should also check the valve has been wire correctly.
White to room thermostat output
Grey to programmer HW OFF and HW cylinder stat Satisfied.
Orange to HW cylinder stat Call and boiler on
Blue to neutral
Earth to earth!
2. Have you checked if the valve spindle is stiff? Remove the actuator and try rotating the valve spindle - it may only move 20° or so from port A open to port B open - depends on the valve. A stiff valve can sometimes be eased with a small amount of WD40 or similar lubricant.
If the valve is OK and wiring OK but the problem is still there, replace the actuator.
Blue to neutral
Earth to earth!
Hi Thanks for the advise I'll check those things out over half term - can you buy just the actuator