16mm twin and earth is fine providing it is adequately protected and volt drop is not excessive.
16 ohms is a bit over the top too. As some of the flats are reading OK it says that the earthing is fine to them from the building MET so the DNO side of it is probably fine. Have a peep in the metering room / cupboard and all will probably be revealed.
A 16mm from building MET to flat MET should be fine, providing of course the Zs is sufficiently low.
Still - even once the main issue is fixed, don't let them get away without sorting main bonding!
Hope this helps - at least it gives you something to go and look at!
Yes, this helps indeed.
Current plan of action.
16mm2 from MET to MET
Forget the existing PEB, and put new one in, visible and all.
test and measure again, and take it from there.
Thanks for the input.