Can you still buy standalone RCD units to go in between the meter and the CU I have a few 100ma ones in my garage, that i inherited from work but i need a 30ma one for a job in a house.
You can still buy them, yes. But they are not considered complaint if fitted between the meter and the CU as there will be a 'single point of failure' in the installation.
In the Eighties, when the Fifteenth was out, best practice often required that a single 30mA RCD protected the entire consumer unit, as a shock prevention measure!
In the Eighties, when the Fifteenth was out (when I first commenced electrical work - 1983/4) CU's did not tend to have RCD's. Instead, best practice was to fit SRCD's adjacent to each external door.
Where an installation incorporates socket outlets rated 32A or less which may reasonably be expected to supply portable equipment for use outdoors, at least one such socket outlet shall be:
(i) placed in a position suitable to supply portable equipment outdoors, and
(ii) marked in accordance with Reg 514-8 ("FOR EQUIPMENT OUTDOORS"), and
(iii) provided with supplementary protection to reduce the risk associated with direct contact by means of an RCD having the characteristics specified in Reg 412-14.