Should ring main live return to same MCB?
4 Feb 2010
Surrey
Hi- have just spotted in my consumer unit that the kitchen ring mains live leaves one 32A MCB and returns to the 32A MCB next to it. (Looks like wire-clamp holes were full). Not my area atall, but just wondering if this is OK. Would both breakers trip with a fault, or, and may be a stupid question, would they act together like a 64A breaker, and therefore need an electrician to rewire? Thanks.
The legs should be in the same mcb, if not you will isolate the circuit by tripping one mcb off but circuit is still live because of the second mcb.
The two should be in the one breaker.
How do you know which wire is which?
One way to check is to switch off one mcb and check if sockets still live. Switch back on and switch off t'other - if still live then likely. Switch off both to confirm the circuit is dead.... and the two legs are split over the mcbs'
SB
The consumer unit is about 20 years old, and the holes for live feed to each mcb are about 4mm wide with 3 twisted cables in, so no more room. I guess there's more space available in more modern ones.
Thanks for the help folks. Without boring anyone any further, I can see the ring (ceiling down), and as helpfully suggested, yup- still live with one mcb off. Now, how do you correct this (or your friendly Part P electrician) if the live cable to be moved doesn't have any space for it in the one mcb clamp? Whole new consumer unit.......? Seems overkill.....
You need an electrician I think!
It could be as easy as moving a wire across, however I very much doubt that!!
You won't need a new CU.
3x 2.5mm cables maximum in each terminal.
So you've got 3 ring finals spread over 2 breakers?
You might be able to get 4 conductors into one MCB - try untwisting them?
Once you've established that the mystery circuit is a ring you're going to have to get it sorted, so if you really cannot get 4 conductors into 1 MCB you'll have to add another MCB into the CU, or replace the CU, or put a 2nd one along side it.
If it's a ring you must do something - leaving it as is is not on.
So if the wires are sorted, I'll have 4 wires to the one mcb, which means 2 ring circuits off one mcb. I guess that is allowed, and I don't need to get a new CU with another 32A point...?
Yes but I strongly recommend you get someone in, it will only cost a few hours.
If you put the cables in the breakers wrongly you will have a cable rated at 20amps that has a mcb protecting it of 32amps.
Also an electrician might be able to rejib the CU and insert another breaker, and issue you with a certificate and part p etc.
I'm guessing you are saying there may be a radial circuit of 2.5mm running on a 32A MCB. nothing wrong there, its in the regs
Where? With T+E? It's compliant if it only feeds a single accessory/socket, but nobody's mentioned that as far as I can see.
I thought that a single socket radial on a 32 amp mcb with 2 existing cables carrying a ring was allowed, but a multiple socket radial that could carry a load in excess of the cable rating wasn't.
The issue is simply that a 2.5mm cable cannot carry 32 amp loads, hence why radial 2.5mm is restricted to a 20 amp mcb.
yep
yep
Highlights again the problems of remote diagnostics and assumptions