I misread the original post - I thought the proposal was to have the earth for connected to the gas pipe, and at another point on the gas pipe have the MET connected.
I have no idea why - sorry...
But I'm not sure I can see a real difference between these two:
You can with both arrangements.The issue will be with 542.4
In this (and in Guidance Note 3) there is a requirement to be able to disconnect the MAIN EARTHING conductor at the MET.
That applies equally to both. Once the cable is disconnected from the rod there's no difference at all between L & R.if at some point, for whatever reason, someone disconnects the earth rod, then the gas becomes the main earth and anyone testing the main earth will still see it as to earth..
He's got a MET, and the gas bonding conductor is connected to it..There are various sections of the 17th edition that refer to this but 542.4.1 specifically mentions that protective bonding conductors shall connect to the main earthing terminal .