http://www.tlc-direct.co.uk/Book/8.6.2.htmHow do you test for Ze ?
http://www.google.co.uk/search?q=ea...tr:countryUK|countryGB&cr=countryUK|countryGBand what type of meter is required
How do you test for Ze ? and what type of meter is required
It's not dangerous when it's plugged in via a socket (like the gas man did)
To the OP - did the guy find >200ohm at all the sockets he tested on?
Were they all part of the same circuit (on the same MCB) or on different socket circuits?
The >200 reading means there is a bad earth at the points he tested at. This could mean the suppliers earth is bad, or the earth wires for the circuits(s) tested are bad.
If the same reading on different circuits then it is likely it is a problem with the suppliers earth, especially if the tested circuits were rings as you need 2 faults/loose wires to break the earth completely in a ring.
How do you conduct an external earth fault loop impedance test via a socket outlet?
Or check Zs, and if not right check R1+R2 at the CU....?The normal procedure would be first to check Ze this is the value as it comes into the house then check Zs this is the value at the socket or other outlet.
then the ELI is well within limits for TT (460 max).
It is actually 500 Ohms max. if you take Uo as 230v.
But either way with anything above 200 it must be ascertained that this is a stable reading and not likely to increase as ground conditions change.
To the op:-
I suggest you seek the services of a competant Electrician
To the op:-
The supply voltage doesn't make any difference, the calculation is on a maximum permissable touch voltage of 50v hence the max Zs for a 100mA RCD is 50v/0.1A=500 ohms
I'll 2nd the need to contact a competent electrician.