IIRC, faults were mainly due to build up of dust and dirt in the RCD. This would not happen if the test button were used on a regular basis (ie not each blue moon).
No. That's wrong as well.I should have said:
Only when the measurements (RA x IΔn ≤ 50V) dictate is a conductive part considered to BE extraneous and so shall be bonded.
Regardless of the calculation to decide whether or not supplementary bonding conductors need to be employed, an extraneous conductive part is an extraneous conductive part, is an extraneous conductive part. As I said, refer to the definition (p.24)
That's it. That's all there is to it.OK I thought I knew but now I'm confused. and very curious.
Page 24 definitions:
"Extraneous-conductive-part. A conductive part liable to introduce a potential, generally Earth potential, and not forming part of the electrical installation."
No. I never even came close to suggesting that this might be the case - this is obviously where you're confused.Are you saying that 'a conductive part NOT liable to introduce a potential' is still called an extraneous conductive part...
I'm surprised you ask this, Bas. There's an excellent book on the subject*: hereOK - so how do you decide if a conductive part is liable to introduce a potential, generally Earth potential, or not?
ProbablyA radiator plumbed into a 100% copper CH system is a e-c-p, yes?
Probably not.What if the pipework is all plastic - is the rad still an e-c-p?
Quite correct, which is why Mr Cockburn's efforts are definitely NOT part of the solution.Better hope they do, because applying bonding to something which is not an e-c-p makes things less safe, not more.
However, is this not just chicken and egg? An object is an e.c.p. therefore must be bonded or an object must be bonded therefore is an e.c.p.