...Rads are 60cm high. My guess is they output about 4kW
and the room requires 5kW-7kW depending on the roof and wall insulation.
Are they doubles of 2300 long?
What temperature could you achieve during the coldspell of minus 8-10?
1. Blocking the chimney would save 1400W
2. Insulating the roof would save 1400W
3. Insulating the walls would save 950W
4. Insulating the floor would save 800W
5. Double glazed UPVC windows and doors would save 570W
Thanks, it's very useful seeing it written down like that. Seems like a no-brainer to get 1-4 done first.
Small point, aren't the reductions quoted more to do with heating design than existing heat output?
The aim is to bring the heating requirement below the available heat output. Of course, it might be possible to increase the radiator size instead.
Sound principle, provided that the money you spend actually brings the solution you are looking for.A householder's first consideration is usually to their wallet. What solutions can be afforded immediately and will cost least in the long run?
You are misinterpreting my figures. The saving I am quoting is the reduction in the required rad size when each option is implemented, assuming that the worst case requires 8.2kW. Maybe I could have explained it better. Does this help?The figures displayed amount to more than the output of the rads in your lounge, which is impossible. Insulation does not produce heat, i.e. you can not save 5000 Watt if you only produce 4500.1. Blocking the chimney would save 1400W
Don't get your hopes up too much...
And you could set the stat in the lounge to 25C, but it would never reach that temperature because the radiators are not large enough for the heat loss. The only possible solutions are:I currently have the stat on 25C with a living room temperature of 17C. If I move the stat to the lounge then I could set the stat to 17C to achieve a 17C lounge temperature.
As for the location of the room thermostat. It doesn't matter where it is, provided each room has the correct size radiator.
Your problem is not the size of the rads, but the fact that your roomstat is in the wrong place.