I don't think anyone is suggesting, or could be suggesting, that there is no neutral. After all, all the affected houses seem to have usable supplies, give or take the RCD tripping.Not without a neutral you wonttbh if it is as easy as go TT, I will be!![]()
Kind Regards, John.
Hi john he has 7 amps flowing through his main earthing conductor that disappears when they connect an earth stake to the MET (it shorts the current flow out) therefore the current flow has to be from the MET
and since this derived from the neutral connection then the current is
flowing from the neutral conductor to ground as apposed to from the neutral conductor back to the star point
he has a broken/high impedence neutral conductor between the transformer and his house
and since he is first to be served by the transformer and the supply is overhead line then there is more than just him that has a faulty neutral
given
this 3A is coming via tho op's neutral conductor from somewhere (neighbouring properties) when it should be heading back along the poles to the transformerthey pulled the service fuses in both houses (and broke ours so a nice new one now) and 3A was still present.
andrew any chance of some pictures of your cutout, main bonding poles etc ?
Matt