A bit of bondage!
Status
Not open for further replies.
From Jan 2012 (I think it is Jan) the requirement for qualified supervisor for the competent person schemes is being increased to NVQ3 (or the new equivalent of NVQ level3)
This guy is about to start his NVQ3.
http://www.diynot.com/forums/viewtopic.php?t=282446&start=0
Is the course going to work miracles?
Great! just read the thread. cmossom has single handedly undermined any confidence I had that things will improve. He appears not to have even a basic education :cry:
Essentially yes but some (or all) RCBOs conforming to BS/EN61009 offer a maximum disconnection time of 300mS at 1X I-delta-N as I understand it.
That is the maximum allowed time for 61008/9 RCDs (non time-delayed)
@ 1x 300ms
@ 5x 40ms
Although, of course, normally less.
@ 1x 300ms
@ 5x 40ms
Yes, I was making the point to Mr Cockburn that you can't make assumptions about earth leakage disconnection times (or any disconnection time for that matter)
He simplistically wrote (and I quote)
"Firstly Sparticus - the RCD trips within 0.04 of a second"
Yes, that is my experience with them too. In general I never see any significant difference during 1X tests between an RCD and an RCBO but I thought it relevant to raise the possibility.
I disagree totally, making something that is electrically floating earthy can make it worse.
Indeed it can. It can also make it better. One has to think about the specific situation and make a intelligent judgement as to which is the greater of opposing risks. To generalise is not, IMO, wise.
IConsider ... (one possible scenario described) ...You can't take into account everyones stupidity when designing an electrical installation - it would drive you insane!
Indeed you can't, but you have to make a judgement as to which scenarios and which types of stupidity may arise, and which are the more likely. It seems that you and I have come to different decisions in the specific scenario I described; that's fine, and doesn't mean that either of us is 'right' or 'wrong'. If there was a claer 'right' and 'wrong', we wouldn't be having this discussion.
As I keep saying, it is necessary to think about the specific scenario, not just generalise.
No, that was my point about arguing both ways. You cannot plan for both.
I wasn't planning for both. I was considering both and then 'designing' on the basis of the one I, IMO, regarded as more likely (even though very unlikely).
There is hardly any likelihood of a live cable touching the bath (and this is not the purpose of bonding) but it is possible for someone leaning on the bath (while not 'having' a bath) to pick up a faulty appliance or frayed lead, for example.
Did I not describe the specific hypothetical scenaio clearly enough? I said that there was no electrical installation anywhere near the bath. In that situation, there would (in the absence of stupidity with extension leads) be no faulty appliance to have a frayed lead. I would therefore regard the possibility of your second scenario as essentially zero, so the first one, even if it had 'hardly any liklihood', would still have more liklihood than the second.
I'm a great believer in having electrical continuity between any metallic parts that can be simultaneously touched, regardless of what the regs may say. If I'm confident that continuity exists because of, say, metallic pipework which I know is always going to be there, then I'm happy with that. If not, out comes the G/Y cable!.
This is where you are going wrong.
There is no difference between a metal table and an isolated bath (or sink, or even BAS' spoon).
It would be less safe if the table were bonded.
If it were an electric table which could become live because of a fault then it would be earthed (or double insulated).
This could be a vacuum cleaner, floor polisher or even a tool being used for repair work in the bathroom.
In case I am missing your point completely, what electrical installation may be near the bath?
Fair enough.
In passing, I think this illustrates how the distinction between earthing and bonding gets a bit confused. Before anyone tries yet again to tell me that I don't understand the difference, let me assure them that I do understand the difference between the purposes of earthing and bonding. However, when you say that the table would be less safe if it were bonded, the reason you say that is not because it would (if bonded) be equipotential with other metallic parts (the purpose of bonding) but, rather, because that bonding would indirectly provide a path to earth. The hazard to which you refer therefore would arise because the bonding would actually 'earth' the table.
I'm starting to wonder whether you believe in the concept of any supplementary bonding. If all required main protective bonding is in place, it would seem that there are only two possibilities for any metallic part within the premises - either it is already (deliberately or otherwise) effectively bonded to MET/CPCs, in which case there's no point in adding supplementary bonding OR it is not connected to the MET/CPC (or anything else to do with the electrical installation!!), in which case it is floating and therefore, per what you have said, should not be bonded. In the presence of satisfactory MPB, there is no way I can think of that it could 'introduce a potential' other than (if so connected) that of the the MET/CPCs.
Kind Regards, John.
Sorry, I didn't realise the point you were making.
Me neither, I thought RCD was just a generic term which includes RCCBs, RCBOs, SRCDs etc.
A RCCB being what most people refer to as an RCD.
Spark123, you are right I think "RCD" is or has become a generic term. I was trying to get Mr Cockburn to realise/acknowledge that you can not make assumptions about disconnection times, that the actual disconnection times are dependant upon the device, the wiring, the "impedance" of the earth fault That a fatal electric shock could be received within the disconnection time.
I got the impression from his comment that all is fine, the RCD will disconnect within 0.04 seconds. I do not hold such faith in these devices and think of them as last resorts rather than a fix-all for poor electrical design. I probably should have written this at the time but I was being intentionally "difficult"  8)
Status