It is something which I thought might occur but had never investigated. On a sketch I have just done my statement is not true. A N-E fault will not affect the operation - in fact it will make the RCD more sensitive.
Most 30mA RCDs operate around the 25mA mark. Say we have a circuit with 1A flowing through the RCD L conductor. 15mA is flowing N-E so we have 0.985A flowing through the RCD N conductor.
Now someone receives a 10mA shock from the L conductor, only 0.975A flows through the RCD N conductor thus causing operation (25mA imbalance) with only a 10mA shock current.
I am in no way advocating N-E faults btw![]()
That is a really interesting thought. For my own understanding if there is a "background" N-E leakage of say 20mA the RCD should sit there and not trip. If a L-E leakage develops, say a 20mA then the differential is zero. So the N-E leakage has essentially raised the RCD trip threshold somewhat? That is, a further 25mA (total 20mA + 25mA = 45mA) may be required to trip the RCD (assuming the RCD will trip with a 25mA differential)? Is my thinking right?