OOI how did you isolate the supply to allow you to connect the CU?I bought the board and RCBO/MCBs new, and have ripped out all the old wiring.
I'd be hugely interested to see how you get onI'm about to start my own re-wire in the summer, but it's a re-wire from scratch, so I'm hoping it might be a little easier than patching an existing installation.
Assuming the SWA is glanded properly is it, and the casing, earthed?Would have liked to have seen earth tag (banjo) on SWA gland.
Why are there two small wires in the 20A MCB - oven?
It is a bit messy.
You appear to have forgotton to apply the numbering sticker for neutral and earth terminals - its probably still in the box.
Normal convention for the MK consumer unit would be to have the main earthing conductor and bonding on the very right
So your neutrals and earthing conductors are difficult to identify which circuits they belong to see reg 514.3.1 - if I had to test that I would be annoyed!
So are you saying your chases are greather than 50mm? Hope they comply with building regs and are not too deep. Vertical chases max one third of wall thickness, horizontal one-sixth of wall thickness.
The supply cable looks like a some 3core SWA (10mm or 16mm) in old colours
I would be interesting to see how the gland is made off.
That's alright then, I just thought they looked smaller (than 2.5) and wondered why two on oven circuit.It's a standard 2.5sqm T&E ring - rated over 20A. That should allow me to have an oven up to about 4.5kW, no? There is nothing else on this ring.
Any howlers before I let building control do their worst...?
Is this the 17th edition you mentioned?
http://www.amazon.co.uk/17th-IEE-Wiring-Regulations-Installations/dp/0750687215
Thanks for any replies.
Cheers,
James
James,
Yes, that's the standard wiring regulations.
In fact, larger than 4.5kW with diversity.