The electrician came this morning and it was indeed a different guy. He spent a couple of hours here testing everything and was very much more thorough than the last.
The 30mA RCDs are not bridged. Both function perfectly and he did a lot of tests from both the CU and various sockets to check. The 100mA RCD refused to trip no matter what he did, which is the opposite to what I expected and hoped to happen (because it would prove a fault if it tripped at a low current, for example).
He replaced the 100mA RCD anyway and could get the new one to trip, so perhaps the old one was somehow faulty.
The only other suspicious behaviour was the N-E resistance was high on every circuit apart from on the kitchen circuit which was 1.3MOhm - low but not low enough to be a problem. It sounds high to me but apparently it's only a problem if it's below 1. These tests were performed with everything unplugged apart from the fridge freezer, which is too heavy to move.