External main protective bonding conductor size
oo7
20 May 2013
Hampshire
Hi guys
Just to double check that if a MPBC is to be surface mounted external to the property we do not have to increase the CSA size?
I've been asked to change a consumer unit and there is currently no MPBCs. The gas meter (external) is about 3 meters away from the wall where the CU can be found, so I intend to make this run of cable external and as far as I can see there is no requirement for additional protection or upping the CSA.
Regarding the water supply the cut of is located in a position where I can't hide the cable or run it up into the ceiling. There's no reason why I can't run this cable in trunking along the skirting?
Cheers,
Chris.
No.
Correct
If by 'cut of(f)' you mean stop-cock it doesn't matter.
The water supply should be bonded at its point of entry to the premises.
  • Thanks
Reactions: oo7
No increase required for external route reason
I've been asked to change a consumer unit and there is currently no MPBCs. The gas meter (external) is about 3 meters away from the wall where the CU can be found, so I intend to make this run of cable external and as far as I can see there is no requirement for additional protection.
It would depend on whether the external location, would/could cause any damaging effects to the cable.
There is no reason you cannot, but remember the regulations say within the property on the consumer side (ideally within 600mm of entry) or where reasonably practicable. They regs do not actually say you need to bond after the internal stop tap!
  • Thanks
Reactions: oo7
To be pedantic the '600mm.' only applies to internal meters; not to the point of entry nor as you say to stop-cocks.
'Where practicable' is quite a leeway but if the point of entry is readily accessible, it would be difficult to justify not fitting it there.
I've lost count of the amount of times that I'd seen externally run bonding cut off and stolen. I'd highly recommend that it is run in containment, rather than clipped direct
Indeed it does, but being pedantic, I didn't mention bonding 600mm from the stop cock or pedantic again the internal stop tap!
If the entry is easily accessible for the bonding conductor yes!
No, I know; that's why I wrote 'as you say'.
However, you did write " (ideally within 600mm of entry)" which I was pointing out is not the case. :)
Many thanks for the clear answers guys.
And yes I did mean stop-cock. :)