Done a job at a large industrial site. Installed two fans (2A FLC) and two starters for them off an existing 3Ph DB which had a spare way.
In the past I had always been under the impression that the EIC should have test results for every submain and sub board right back to the origin. Well on this job, that is simply not possible because the board we connected into is on about 3 Submains, fed from a switch fuse and busbar chamber.
We are simply not going to be able to shut down the entire plant to take these readings and take a Ze at the origin. I know the Ze could be noted from enquiry and put on the EIC, but what would you do in this situation? Is it OK to just have the new circuit we installed and the details of the origin, and note this on the EIC?