mistake
[I'm glad I'm not the only person that happens tomistake
Well, in terms of my understanding (which seems to me to be a common sense one) of what CCC/Iz means, the answer in both cases is 27A (assuming no other de-rating factors) - and it would still be 27A for any type of OPD with any In. As far as I am concerned "CCC" (or Iz) means exactly what it says - and, for a given cable installed in a given way, will be the same whether it is protected by a 6A OPD or a 100A OPD, and whether it's protected by an MCB or a 3036 fuse. Of course, some of those OPDs would not allow 27A to flow for very long (or may allow a lot more than 27A to flow for a long time), but that would not alter the "current-carrying capacity" of the cable, as installed.I wrote a long answer but then I stumbled upon what I think you are getting at but I can't explain it, either. Please answer this:
A ring circuit with 2.5mm² cable to method C -
What IS the Iz of the cable with a 32A MCB?
What IS the Iz of the cable with a 30A 3036?
Yes, along with the rest of your post, that's what I realised (I think) you were getting at.Well, in terms of my understanding (which seems to me to be a common sense one) of what CCC/Iz means, the answer in both cases is 27AI wrote a long answer but then I stumbled upon what I think you are getting at but I can't explain it, either. Please answer this:
I'm glad that you now at last understand what I've been saying.Yes, along with the rest of your post, that's what I realised (I think) you were getting at.Well, in terms of my understanding (which seems to me to be a common sense one) of what CCC/Iz means, the answer in both cases is 27APlease answer this: A ring circuit with 2.5mm² cable to method C -
What IS the Iz of the cable with a 32A MCB? What IS the Iz of the cable with a 30A 3036?
IndeedHowever, if the cable were installed in conduit for part of its run then the Iz of the cable would reduce to 20A (correct?).
I presume you must be talking about a ring final, since a cable in a radial with a CCC of 20A protected by a 32A MCB obviously would not be acceptable.The MCB circuit would still be compliant ....
THAT is the very issue/question I've been addressing all along. In common senses terms, I agree that a Method A 2.5mm² ring protected by a 30A 3036 ought not to be acceptable. However, if you now accept 'my' definition of CCC/Iz, and if you accept that such is the meaning of "current-carrying capacity" in both 433.1.202 and 433.1.204, then the wording of 433.1.204 appears to be saying that a Method A 2.5mm² ring protected by a 30A 3036 is just as acceptable as the same circuit protected by a B32. That has been the point I've been trying to make all along. I agree that it does not make electrical sense, but it appears to be what the regulation is saying.... but the 3036 circuit would not.
As above, you're trying I talk electrical common sense. What I've been discussing, all along is what 433.1.204 actually says.If not wishing to reduce the 3036 In to 14.5A (10A or 15A?), do you agree that the cable would have to be increased to one with a method A CCC of (20/0.725) 27.6A? I.e. 6mm² where its Iz would still be 32A.
I don't think so. Provided we stick with using CCC/Iz to 'mean what it says' (i.e. don't adjust it for OPD type) everything is fairly clear, and it's then up to 433.1.204 to decide what degree of 'under-protection' (as compared with what would be required in a radial) is acceptable in a ring. The one thing seemingly 'wrong' with 433.1.103, as worded, (at least, per my interpretation) is that it appears to say that one can have "20A CCC" ring ('my' meaning of CCC) protected a 30A 3036 or a 32A MCB. If that was changed to "20A 3036 or 32A MCB, it would probably be about right - and would be roughly 'equivalent' to the corresponding situation with radials.Do we need another term instead of Iz for this situation, i.e. rings?
I'm with you electrically. However, I'm suggesting that what the words of the reg actually says is not what it should say (in terms of electrical common sense)I'm still not comfortable with your reasoning because of what the regulations might actually say, nor usually are you.
The short answer is 'no' - I believe that CCC/Iz relates to how much current a cable can safely carry (under the particular installation conditions), regardless of what (if anything) is protecting it. The cable surely still has the same 'CCC' even if its not protected at all!Do you not consider "under the particular installation conditions concerned" (in Iz definition) to include the OPD?
Yes, but usually you would be arguing against the wording, not for the thing it seems to allow.]I'm with you electrically. However, I'm suggesting that what the words of the reg actually says is not what it should say (in terms of electrical common sense)
It does, but must have a lower Iz, or whatever it may be called, so that the possible overload can be safely handled.The short answer is 'no' - I believe that CCC/Iz relates to how much current a cable can safely carry (under the particular installation conditions), regardless of what (if anything) is protecting it. The cable surely still has the same 'CCC' even if its not protected at all!
I still do not understand why you think it would be done twice.Whatever, as I keep saying in support of my view, if 'your' interpretation were correct, such that you had to multiply the tabulated It by 0.725 to get 'CCC' when the OPD was a 3036, 433.1.202 would then cause you to multiple that (already multiplied by 0.725) figure by a second 0.725 - which is obviously wrong.
You're still misunderstanding me. I agree with you about what should (and should not) be allowed - I am suggesting that the wording of 433.1.204 appears to allow something that neither you nor I believe should be allowed. I am not 'arguing for' the thing which the words of the reg appears to be allowing (I would say wrongly).Yes, but usually you would be arguing against the wording, not for the thing it seems to allow.]I'm with you electrically. However, I'm suggesting that what the words of the reg actually says is not what it should say (in terms of electrical common sense)
No. As I keep saying, it's nothing to do with characteristics of the cable (CCC/Iz). It's simply a matter that, with some OPDs, the maximum In of the OPD to give adeqaue protection to a cable of a particular CCC is lower than would be the maximum In requird for some other type of OPD. Nothing to do with the cable or its CCC/Iz changing with different OPDs.It does, but must have a lower Iz, or whatever it may be called, so that the possible overload can be safely handled.The short answer is 'no' - I believe that CCC/Iz relates to how much current a cable can safely carry (under the particular installation conditions), regardless of what (if anything) is protecting it. The cable surely still has the same 'CCC' even if its not protected at all!
With the view you expressed (and with which I disagree) "current-carrying capacity" would be obtained by multiplying the tabulated It by 0.725 if protection is by 3036 - hence for 2.5mm² Method C about 19.6A (27A x 0.725). 433.1.102 then says that if protection is by a 3036, it's In must not be greater than 0.725 times the "current-carrying capacity" (which, in previous sentence, you would have calculated as ~19.6A). You would therefore conclude that the In of the 3036 could not be greater than about 14.2A (19.6A x 0.725) - which is clearly wrong, and results from your having multiplied by 0,725 in the previous sentence and (per 433.1.202) by 0.725 in this sentence. That's twiceI still do not understand why you think it would be done twice.Whatever, as I keep saying in support of my view, if 'your' interpretation were correct, such that you had to multiply the tabulated It by 0.725 to get 'CCC' when the OPD was a 3036, 433.1.202 would then cause you to multiple that (already multiplied by 0.725) figure by a second 0.725 - which is obviously wrong.
The entire discussion is about ring circuits, since all I'm talking about is the wording of 433.1.204!I think all the confusion is the result of the anomalies of ring circuits.
Yes, 46.4A for an hour through the MCB, but the whole concept of the ring is that a lot less than that ('ideally' only a half) would go through the cable in either leg of the ring. Someone has decided that, in a ring, it is acceptable for the OPD's In to be 1.6 times greater than the maximum which would be allowed for a radial (i.e. a 32A MCB protecting a cable with CCC=20A).The only true comparison would be a 2.5mm² ring installed to method A (if anyone were daft enough to do it). This would consist of the (minimum allowed size) cable actually having the (minimum allowed) CCC and Iz of 20A. With a 32A MCB this would have allowed for a current of 46.4A (32A x1.45) for an hour without damage.
Quite, that would be a 'dispensation ratio' (ring/radial) of 3.0 (60/20), as compared with the 1.6 'allowed' with an MCB - and clearly far too great. That's why I believe that 433.1.204, as worded, is wrong.It clearly would not be satisfactory with a 30A 3036 where the current may be 60A (30A x2) for an hour.
I'll point out, for the last time (and I'll use big letters as you don't seem to have seen it before)I have employed a sparky and come to an agreement that I will chase all the walls sockets and run wire in as long as he connects ALL sockets and CU and tests!
This is to reduce cost, but also give me the relevant certification I need!
No, but nor did you ever say it was, despite being asked. And you did begin here asking questions which showed that you were not competent to be doing the electrical work yourself and that you didn't have anyone involved who was.DID I EVER MENTION IT WASNT AGREED?