is 2.5mm2 cable fine from cooker switch to CCU?
3 May 2015
Yorkshire
From the CCU there will be a new induction hob and cooker.
Depends on the electrical kW rating of the appliances, but generally I would say using 2.5 mm2 cable between the cooker switch and the so callled CCU would be foolish.
Foolish because adding even bigger appliances later would be difficult.
In fact, it sounds woefully too small already, so don't even consider it.
Stick to size of the cable used to feed the cooker switch.
I would expect this to be a minimum of 6.0 mm2, in some rare cases 10.0 mm.
If you are reluctant in buying a reel of cable, find a place that sells small quantities or does it by the metre.
If you mean would it be acceptable to install 2.5mm T&E between the Cooker Control Unit and the outlet plate of the oven and hob.
I would say not!
Induction hobs are rarely rated at less than 20A and you would expect even a low output oven to repair a 13A fuse.
I know it could be argued, that the demand maybe not be a constant.
But in this scenario, I would be putting 6mm cable in, which would allow for a demand up to 15kW, for any future proofing.
If you mean would it be acceptable to install 2.5mm T&E between the Cooker Control Unit and the outlet plate of the oven and hob. I would say not!
I agree that it would make little sense, and that it would not be acceptable/compliant if the circuit were protected by a 32A MCB, given that the peak current demand of the cooking appliances would almost certainly exceed the CCC of the cable.
Induction hobs are rarely rated at less than 20A and you would expect even a low output oven to repair a 13A fuse. ... I know it could be argued, that the demand maybe not a constant.
True. If the total load was, as you suggest, around 33A, that would, as you imply, after application of diversity, be a small enough load to be supplied by 2.5mm² cable protected by a 20A MCB ... but that would not really make much sense - particularly if most of the circuit is already wired in 6mm² or 4mm² cable.
That would be the conventional approach. Given ideal (Method C) cable installation, 4mm² cable (with a 32A MCB) would theoretically be adequate - and, as you say, would be more than adequate for any future requirements (up to 19kW of cooking appliances, if there were no additional socket supplied by the circuit).
I have now installed 6mm2 makes sense to follow it through... I have another question though is it ok to connect cables together using blocks and just wrap in proper tape or do they have to be in a plastic box?
Hi, use a dual appliance outlet that's what they are designed for. :)
Regards,
DS
I mean linking cable to cable to before its reached the switch as it isn't long enough?
I would advise you replace the cable with one piece the correct length.
DS
It goes deep behind the plaster board so want to keep the damage to s minimum would it still pass regs?