Cross sectional area current capacity
26 Apr 2015
How would one determine the current carrying capacity of 2.08mm2 conductor?
I dont think those are accurate, or would comply with the regs. For example 2.08 seems to be listed at 15 amps, but that is obviously based on method 101 as 1.5 is already 15 amps for installation method A. Dont the regs base the values off a certain equation? Either that use the current value inbetween 1.5mm and 2.5mm2.
I presume they are accurate for AWG and the US - AWG 12 (2.05mm²) 20A.
The maximum for 1.5mm² T&E is 20A but it is a different cable and conductor.
I dont think so. I did some digging and found this. 12 gauge is 3.31 mm2. This wire here is 2.08mm2.
Found this, but I can't say how it relates to UK CCC's though. Realistically I'd treat it more like 1.5mm than 2.5mm
Is this wiring existing? Do you HAVE to use it or can you replace it?
No published equation that we are aware of. However, if you look at the second post from me on this page of a recent thread, you will see that the BS7671 (Table 4D5) Method C CCC figures can be closely modelled by:
CCC = 15.774 x CSA^0.6077
... for a 2.08mm² conductor, that would give a (Method C) CCC of about 24.6A. Mind you, I don't know that an inspector or person doing an EICR would accept my modelling, so it might be safer to assume, conservatively, that it's 1.5mm² !!
Perhaps they are inaccurate. I was only going by the first link.
Thanks! That is what I was looking for. :) I think it does hold some value in my opinion.
However this equation only works for clipped direct I take it? What would it be reduced to when using other methods like method A? And the power curve is based on a 70*C conductor operating temperature?
You're welcome - but, as I said, I'm not sure whether 'third parties' would necessary accept my figures :)
Yes, as I said, it's a modelling of (Method C) of Table 4D5 - so, yes, 70°C conductor temperature. If I had the time, I could try modelling Method A. However, looking at Table 4D5, the difference between Method C and Method A is always a factor of between 1.35 and 1.49 (1.38 for 1.5mm² and 1.35 for 2.5mm²), so if you divided the Method C figure by 1.49 (to be safe/conservative) or by 1.38 (based on the 1.5/2.5mm² figures), you wouldn't be far off - so, for 2.08mm² Method A (70°C), that would be about 16.5A (or 17.8A).
That makes sense. Now my understanding is the factor is less restrictive for 1.5mm2 because smaller conductors can dissipate heat better? Or is it the other way around? Correct to think that heat dissipation of 2.08mm2 is in between 1.5mm2 and 2.5mm2?
Edit: just to confirm, by 1.35 you mean 1.38? My apologies.
Yes, I suppose that's got to be true to some extent, but there's hardly any difference between 1.35 and 1.38, so one might as well 'be conservative'! However, I also suspect that some of the small variation in the de-rating factors (from 1.39 for 1mm² {yes, fractionally higher than 1.5mm² and 2.5mm²} to 1.49 at 16mm²) may be as much to do with rounding as anything else.